    i attached a manifold gauge set and took some readings on it:

    static (after the car was shut off):
    high 92
    low 93

    temperature outside was 89 degrees farenheight.

    running (the compressor was engaging for 3 seconds on, 3 seconds off)
    high 140-155
    low 22-42.

    anyone wanna guess.
    "..Torchinski v. Peterson that it is legal to carry a concealed weapon, so long the weapon is totally slick like a huge ass machine gun that you carry under a trench coat, like in the Matrix."


  2. #2
    Join Date
    Feb 2004
    Posts
    4,894

    Default

    The low and high pressure is right... I am guessing you got too much refrigerant which triggers the high side cutoff when it hits 42 PSI. If you don't mind, let some pressure out when the system is off... let it go down to 85 PSI static.

    Low should be rock steady at 28-30 PSI.

    Your compressor is working properly.

  3. #3
    Join Date
    Nov 2006
    Location
    Germany
    Posts
    475

    Default

    Quote Originally Posted by ryan roopnarine View Post
    i attached a manifold gauge set and took some readings on it:

    static (after the car was shut off):
    high 92
    low 93

    temperature outside was 89 degrees farenheight.

    running (the compressor was engaging for 3 seconds on, 3 seconds off)
    high 140-155
    low 22-42.

    anyone wanna guess.
    Those numbers are low, especially the high side for such a warm day. This most likely means low freon level. I figure a low side of 35-45 w/ high side of 250-325 is about right...

    What did the sight glass look like while the compressor was running? I figure very frothy...on a 'solid' system, it should be solid liquid only.

    I take the rad fans were running? Or do they cycle with the compressor? Either way, once you get the system to hold freon, ensure the fan(s) run with the compressor.

    Brian

  4. #4
    Join Date
    Feb 2004
    Posts
    4,894

    Default

    Good point about the aux fan... it must be running when AC is switched on.

    For R134a, you want the low pressure to be 28 to 30 PSI.

  5. #5
    Join Date
    Jan 2004
    Location
    Benneton (United Colors of)
    Posts
    3,067

    Default

    1 evacuation and one vacuum later...
    system holds between 29-30 inches HG over 17 hours. the drop might be because i disconnected and reconnected everything.

    in went one 12oz can of leak detector r134a
    1 2/3 can of regular freon (capacity is 32oz/.96kg)

    about 90-94 deg f today, it feels cold, but as though something is missing. i only noted that the engine fan came on with the ac, i don't know if there have to be special circumstances for the other fan to come on.

    reads 42lb low
    and 230 high. don't want to overcharge the thing, because i don't have a refrigerant scale. should i try to fit the other can in?

    thanks for your help.
    "..Torchinski v. Peterson that it is legal to carry a concealed weapon, so long the weapon is totally slick like a huge ass machine gun that you carry under a trench coat, like in the Matrix."


Similar Threads

  1. OT: generic car q--99 ford taurus and oil pressure
    By ryan roopnarine in forum 5 Series BMW
    Replies: 11
    Last Post: 07-29-2009, 10:42 AM
  2. OT -new Taurus has M5 vents!
    By Russell in forum 5 Series BMW
    Replies: 2
    Last Post: 07-03-2007, 01:04 AM
  3. Replies: 6
    Last Post: 12-11-2005, 12:51 PM
  4. OT: sputtering problem in 99 ford taurus (3.0 OHV VULCAN)
    By ryan roopnarine in forum 5 Series BMW
    Replies: 2
    Last Post: 05-07-2005, 09:33 PM
  5. Replies: 8
    Last Post: 10-07-2004, 10:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •